mayoorite
mayoorite Original post #1
Jun 28, 2011 at 6:35 AM
i have bought br600ci-in APC UPS in April 2010 and in the beginning it gave backup of 9-10 minutes. But after a month or two it gave 1 minute backup only.So i called up the company and they replaced it.Again same thing happens after 2 months and again they replaced. Now they have replaced it three times but now same thing is happening . I have checked my power supply by an electrician and it is perfectly OK.My Pc is old therefore it gives only 10 minutes backup. I have kept ups on charging for 2 days but nothing happened.

:-(
Please help me.
thetechfreak
Jun 28, 2011 at 7:27 AM
I think you might have overloaded it with connecting everything to it. Whats your full config?
mithun_mrg
Jun 28, 2011 at 7:38 AM
Also check ur earthing and Grid Voltage
mayoorite
Jun 28, 2011 at 7:03 PM
Pentium 4 2.4 GHz Northwood ,500 GB Segate HDD,2 GB DDR RAM ,CRT Monitor syncmaster 753s,ADCOM Speakers.

I have only plugged monitor , cpu and modem in ups
mithun_mrg
Jun 29, 2011 at 7:27 AM
Try using ony the CPU plugged in the UPS Plug the monitor to GRID using a spike guard or Voltage Stabilizer and see the backup time