APC UPS. not working

13 posts · originally from https://geek.digit.in/community/threads/apc-ups-not-working.166890/

B
ballyrick Original post #1
Nov 29, 2012 at 1:48 AM
hi.
i am after pulling a old ups out of storage and trying to get it working again.
its a APC smart ups 700 series. model no. su700inet.
when i plug in the ups (with & without load) the overload light comes on and the ups emits a loud tone. the battery has two bars left in it and the fuse is not pushed out at the back.
i have searched online and there hasn't been much there for this problem. one forum says to replace the overload relay. i have opened the ups and found the relay it seems to be fine. the relay is a SCHRACK RP920124.
thanks in advance to everyone that helps.
rick
Myth
Myth #2
Nov 29, 2012 at 3:40 PM
If the battery is old then it might need to be replaced.
B
Nov 29, 2012 at 10:46 PM
If the battery is old then it might need to be replaced.

Thanks "myth" for your reply. however i have looked at buying a battery pack but it will cost over €50 and what if the ups still doesn't work after that?
I think that the battery has nothing to do with this problem because it shows two bars for battery health.
kind regards
rick
Myth
Myth #4
Nov 29, 2012 at 11:39 PM
Call up the apc customer care and ask them what to do. Is it within the warranty period ?
Or else take it to the apc service centre.
B
Nov 30, 2012 at 1:01 AM
Call up the apc customer care and ask them what to do. Is it within the warranty period ?
Or else take it to the apc service centre.

i contacted them via chat and the rep hadn't a clue. she was just reading the Faq.
the ups is out of warranty. the rep said that i can either trade it in or get it repaired but she wouldn't say how much it would cost.
S
Nov 30, 2012 at 5:26 AM
Try turning on the UPS without the battery.. and see what happens..
B
Nov 30, 2012 at 10:40 PM
Try turning on the UPS without the battery.. and see what happens..

i gave that a go and nothing happens. no tone or lights.

also i am after contacting apc via email and i was told to do a "dead brain test".
by plugging out the ups and holding the off button for 6 seconds. i should hear a click and see a flash of lights. this will reset the overload warning.
however the test never worked for me. i could never hear the click or see the flash of lights.
thetechfreak
Dec 7, 2012 at 10:34 AM
Well you don't really have many options now. Would recommend you to take it to an authorized service center and get it checked out.

Also is the Earthing at your place proper? Many UPS go kaput because of bad Earthing too.
B
Dec 8, 2012 at 3:08 PM
Also is the Earthing at your place proper? Many UPS go kaput because of bad Earthing too.

i have never had any problems with the earthing here, so i'm not sure.
when the call centers open again ill ask them where is my authorized service center because i'm not sure where it is.
i am going to get a battery pack from a friend and see if that fixes the problem.
B
ballyrick #10
Dec 10, 2012 at 2:15 AM
Just got back from a friends house where i pluged in another battery and
IT Worked.

The battery must have been damaged or the voltage was too low.
Thanks everyone who helped me in the search for a solution.

Kind Regards
Ricky
B
ballyrick #11
Dec 19, 2012 at 1:38 AM
Hi all.

I got the batteries last weekend, and they fit in fine and connect however.
When i plug in the batteries and turned on the ups. the lights come on like they should but the overload light comes on again.
What is happening now is a bit different to what happened before i put in the new batteries.

I have uploaded a video showing what happens. APC Ups overload problem - YouTube
The video shows what happens when NO load is connected, the same thing happens when plugged out and still NO load connected.
When i connect a load no power gets through and the same process happens but a lot faster.

Thanks in advance for any help.

Kind Regards
Rick
Myth
Myth #12
Dec 19, 2012 at 1:06 PM
Have you charged your new battery for the number of hours specified in manual ?

PS: I cant view those videos from office(goddamn websense !!), so making an assumption here.
B
ballyrick #13
Dec 19, 2012 at 1:27 PM
I tried the batteries when i got them first and then after charging to 14.90v on each.

PS: Did you try using a proxy server or vpn to your home.